Apis, if it draws 40 amps on 2 legs, it is drawing 20 amps from each leg. Adding the third phase will reduce the draw to 13.333 amps per leg, still totaling 40 amps. With 13.3 amps producing less friction and heat, it will actually reduce the total power draw and reduce the power bill rather than increase it. You can run the machine on 3 fuses, 15 amp each if the start up surge will take it.